Here is a short run-through of how lead-acid batteries work. I'll start with some basics.

Voltage

Voltage is an electrical measure which describes the potential to do work. The higher the voltage the greater its risk to you and your health. Systems that use voltages below 50V are considered low-voltage and are not governed by an as strict (some might say arcane) set of rules as high-voltage systems.

Current

Current is a measure of how many electrons are flowing through a conductor. Current is usually measured in amperes (A/Amps). Current flow over time is defined as ampere-hours (a.k.a. amp-hours or Ah), a product of the average current and the amount of time it flowed.

Power

Power is the product of voltage and current and is measured in Watts. Power over time is usually defined in Watt-hours (Wh), the product of the average number of watts and time. Your energy utility usually bills you per kiloWatt-hour (kWh), which is 1,000 watt-hours.

Lead-Acid Battery?

A lead-acid battery is a electrical storage device that uses a reversible chemical reaction to store energy. It uses a combination of lead plates or grids and an electrolyte consisting of a diluted sulphuric acid to convert electrical energy into potential chemical energy and back again. The electrolyte of lead-acid batteries is hazardous to your health and may produce burns and other permanent damage if you come into contact with it. So, when dealing with electrolyte protect yourself appropriately.

Deep Cycle vs Starting Batteries

Batteries are typically built for specific purposes and they differ in construction accordingly. Broadly speaking, there are two applications that manufacturers build their batteries for: Starting and Deep Cycle.

• As the name implies, Starter Batteries are meant to get combustion engines going. They have many thin lead plates which allow them to discharge a lot of energy very quickly for a short amount of time. However, they do not tolerate being discharged deeply, as the thin lead plates needed for starter currents degrade quickly under deep discharge and re-charging cycles. Most starter batteries will only tolerate being completely discharged a few times before being irreversibly damaged.

Deep Cycle batteries have thicker lead plates that make them tolerate deep discharges better. They cannot dispense charge as quickly as a starter battery but can also be used to start combustion engines. You would simply need a bigger deep-cycle battery than if you had used a dedicated starter type battery instead. The thicker the lead plates, the longer the life span, all things being equal. Battery weight is a simple indicator for the thickness of the lead plates used in a battery. The heavier a battery for a given group size, the thicker the plates, and the better the battery will tolerate deep discharges.

• Some Marine batteries are sold as dual-purpose batteries for starter and deep cycle applications. However, the thin plates required for starting purposes inherently compromise deep-cycle performance. Thus, such batteries should not be cycled deeply and should be avoided for deep-cycle applications unless space/weight constraints dictate otherwise.

Regular vs Valve-Regulated Lead Acid (VRLA) Batteries

Battery containers come in different configurations. Flooded batteries can be either sealed or open.

Sealed flooded cells are frequently found as starter batteries in cars. Their electrolyte cannot be replenished. When enough electrolyte has evaporated due to charging, age, or just ambient heat, the battery has to be replaced.

Deep-Cycle flooded cells usually have removable caps that allow you to replace any electrolyte that has evaporated over time. Take care not to contaminate the electrolyte - wipe the exterior container while rinsing the towel frequently.

- VRLA batteries remain under constant pressure of 1-4 psi. This pressure helps the recombination process under which 99+% of the Hydrogen and Oxygen generated during charging are turned back into water. The two most common VRLA batteries used today are the Gel and Absorbed Glass Mat (AGM) variety.

Gel batteries feature an electrolyte that has been immobilized using a gelling agent like fumed silica.

AGM batteries feature a thin fiberglass felt that holds the electrolyte in place like a sponge.

- Neither AGM or Gel cells will leak if inverted, pierced, etc. and will continue to operate even under water.

Battery Cells

Battery Cells are the most basic individual component of a battery. They consist of a container in which the electrolyte and the lead plates can interact. Each lead-acid cell fluctuates in voltage from about 2.12 Volts when full to about 1.75 volts when empty. Note the small voltage difference between a full and an empty cell (another advantage of lead-acid batteries over rival chemistries).

Battery Voltage

The nominal voltage of a lead-acid battery depends on the number of cells that have been wired in series. As mentioned above, each battery cell contributes a nominal voltage of 2 Volts, so a 12 Volt battery usually consists of 6 cells wired in series.

State of Charge

The State of Charge describes how full a battery is. The exact voltage to battery charge correlation is dependent on the temperature of the battery. Cold batteries will show a lower voltage when full than hot batteries. This is one of the reasons why quality alternator regulators or high-powered charging systems use temperature probes on batteries.

Depth of Discharge

The Depth of Discharge (DOD) is a measure of how deeply a battery is discharged. When a battery is 100% full, then the DOD is 0%. Conversely, when a battery is 100% empty, the DOD is 100%. The deeper batteries are discharged on average, the shorter their so called "cycle life".

Battery Storage Capacity

The Amp-hour (Ah) capacity of a battery tries to quantify the amount of usable energy it can store at a nominal voltage. All things equal, the greater the physical volume of a battery, the larger its total storage capacity. Storage capacity is additive when batteries are wired in parallel but not if they are wired in series.

Most marine, automotive, and RV applications use 12V DC. You have the choice to either buy a 12V battery or to create a 12V system by wiring several lower-voltage batteries/cells in Series.

Battery Wiring

When two 6V, 100Ah batteries are wired in Series, the voltage is doubled but the amp-hour capacity remains 100Ah (Total Power = 1200 Watt-hours).

You may decide to wire batteries in series because a single 12V battery with the right storage capacity is simply too heavy, unwieldy, or awkward to lift into place. Batteries consisting of fewer cells (and hence lower voltage) in series can provide the same storage capacity yet be portable. It is not unusual to see solar power installations where the battery bank consists of a sea of 2V batteries that have been wired in series

series.jpg

Two 6V, 100Ah batteries wired in Parallel will have a total storage capacity of 200Ah at 6V (or 1200 Watt-hours).

Battery banks consisting of 12V batteries wired in parallel are often seen on OEM installations in boats and RVs alike. Such banks are simple to wire up and require a minimum of cabling. However, the wiring must have the capacity to deal with a full battery bank.

You should fuse each battery individually in such a bank to ensure that a battery gone bad will not affect the rest of the bank.

parallel.jpg

Battery banks wired in Series-Parallel are even more complicated. Here, four 6V cells are wired in two "strings" of 12VDC that were then wired in parallel. Using 6V, 100Ah batteries, this system will have a storage capacity of 200Ah at 12V or 2,400Wh.

Since such a system has more wiring, it is very important to group "strings" logically and to label everything. Furthermore, it is a very good idea to fuse every "string" of series-wired batteries to ensure that a problem in one part of the battery bank does not take the whole bank down.

Group GPL4C batteries are exclusively used on boats. Since these batteries have a nominal voltage of 6V, we have wired them in series for the starter bank (2 batteries) and series-paralell for the house bank (4 batteries).

Despite advances in instrumentation, the battery industry mostly still advertises amp-hours as a capacity measure instead of watt-hours. Hopefully, the battery and marine power instrumentation industry will make a transition to Watt-hours (Wh) in the future.

series-parallel.jpg

Link to comment
Share on other sites

Available Capacity vs Total Capacity

Since batteries depend on a chemical reaction to produce electricity, their Available Capacity depends in part on how quickly you attempt to charge or discharge them relative to their Total Capacity. The Total Capacity is frequently abbreviated to C and is a measure of how much energy the battery can store. Available Capacity is always less than Total Capacity.

Typically, the amp-hour capacity of a battery is measured at a rate of discharge that will leave it empty in 20 hours (a.k.a. the C/20 rate). If you attempt to discharge a battery faster than the C/20 rate, you will have less available capacity and so on. The more extreme the deviation from the C/20 rate, the greater the available (as opposed to total) capacity difference.

However, this effect is non-linear. The available capacity at the C/100 rate (100 hours to discharge) is typically only 10% more than at the C/20 rate. Conversely, a 10% reduction in available capacity is achieved just by going to a C/8 rate (on average). Thus, you are most likely to notice this effect with engine starts and other high-current applications like inverters, windlasses, desalination, or air conditioning systems.

For example, the starter in an engine will typically quickly outstrip the capacity of the battery to keep cranking it for any length of time. Hence the tip from mechanics to wait some time between engine start attempts. Not only does it allow the engine starter to cool down, it also allows the chemistry in the battery to "catch up". As the battery comes to a new equilibrium, its available capacity increases. A very elegant equation developed in 1897 by a scientist called Peukert describes the charging and discharging behavior of batteries.

As you can see below, the Peukert equation consists of several factors.

Peukerts Equation: In x T = C where

l is the current (usually measured in amperes)

T is time (usually measured in hours)

n is the Peukert number / exponent

C is the theoretical storage capacity of the battery (usually measured in amp-hours). Use the C/100 capacity or add 10% to the storage capacity at the C/20 rate.

As you can see, the available current is dependent on the rate of discharge and the Peukert exponent for the battery. The closer the exponent is to 1 (one), the less the available capacity of a battery will be affected by fast discharges. Peukerts numbers are derived empirically and are usually available from manufacturers. They range from about 2 for some flooded batteries down to 1.05 for some AGM cells. The average peukerts exponent is 1.2 though the exact number depends on the battery construction and chemistry.

(Hope what you just read made sense lol)

Reserve Minutes

Reserve Minutes are a measure of how long your battery can sustain a load before it's available capacity has been completely used up. This measure is especially useful for folks who want to run inverters, fridges, and other large loads.

Conversion Efficiency

The conversion efficiency denotes how well a battery converts an electrical charge into chemical energy and back again. The higher this factor, the less energy is converted into heat and the faster a battery can be charged without overheating (all other things being equal). The lower the internal resistance of a battery, the better its conversion efficiency.

One of the main reasons why lead-acid batteries dominate the energy storage markets is that the conversion efficiency of lead-acid cells at 85%-95% is much higher than Nickel-Cadmium (a.k.a. NiCad) at 65%, Alkaline (a.k.a. NiFe) at 60%, or other inexpensive battery technologies.

Battery Life

Battery manufacturers define the end-of-life of a battery when it can no longer hold a proper charge (for example, a cell has shorted) or when the available battery capacity is 80% or less than what the battery was rated for. The life of Lead Acid batteries is usually limited by several factors:

Cycle Life is a measure of how many charge and discharge cycles a battery can take before its lead-plate grids/plates are expected to collapse and short out. The greater the average depth-of-discharge, the shorter the cycle life.

Age also affects batteries as the chemistry inside them attacks the lead plates. The healthier the "living conditions" of the batteries, the longer they will serve you. Lead-Acid batteries like to be kept at a full charge in a cool place. Only buy recently manufactured batteries, so learn to decipher the date code stamped on every battery... (inquire w/manufacturer). The longer the battery has sat in a store, the less time it will serve you! Since lead-acid batteries will not freeze if fully charged, you can store them in the cold during winter to maximize their life.

Sulphation is a constant threat to batteries that are not fully re-charged. A layer of lead sulphate can form in these cells and inhibit the electro-chemical reaction that allows you to charge/discharge batteries. Many batteries can be saved from the recycling heap if they are Equalized

Equalization

Sulphation layers form barrier coats on the lead plates in batteries that inhibit their ability to store and dispense energy. The equalization step is a last resort to break up the Sulphate layers using a controlled overcharge. The process will cause the battery electrolyte to boil and gas, so it should be only done under strict supervision and with the proper precautions.

Gassing

Batteries start to gas when you attempt to charge them faster than they can absorb the energy. The excess energy is turned into heat, which then causes the electrolyte to boil and evaporate. The evaporated electrolyte can be replenished in batteries with removable caps such as most flooded deep cycle batteries. Many car batteries are sealed and thus need to be replaced when their electrolyte evaporates over time.

Since AGM and Gel cells are always sealed, it is very important to guarantee they are not overcharged. The only way to ensure this is to use a temperature-compensated charging system. Such chargers use a temperature probe on the battery to ensure that the battery does not get too hot. As the battery heats up, the charging current is reduced to prevent thermal runaway, a very dangerous condition.

Thermal Runaway

This is a very dangerous condition that can occur if batteries are charged too fast. One of the byproducts of Gassing are Oxygen and Hydrogen. As the battery heats up, the gassing rate increases as well and it becomes increasingly likely that the Hydrogen around it will explode.

Self Discharge

The self-discharge rate is a measure of how much batteries discharge on their own. The Self-Discharge rate is governed by the construction of the battery and the metallurgy of the lead used inside.

For instance, flooded cells typically use lead alloyed with Antimony to increase their mechanical strength. However, the Antimony also increases the self-discharge rate to 8-40% per month. This is why flooded lead-acid batteries should be in use often or left on a trickle-charger.

The lead found in Gel and AGM batteries does not require a lot of mechanical strength since it is immobilized by the gel or fiberglass. Thus, it is typically alloyed with Calcium to reduce Gassing and Self-Discharge. The self-discharge of Gel and AGM batteries is only 2-10% per month and thus these batteries need less maintenance to keep them happy.

Battery Group Size

To further complicate matters, manufacturers for marine batteries make them in all sorts of sizes and voltages. Battery case sizes are typically denoted by a "Group Size" which has nothing to do with the actual size of the battery. For example, Group 8D batteries are much larger than Group 31 batteries.

Table of Battery Group Sizes, Voltages, and Approximate Exterior Dimensions

battgroups.jpg

The group size will merely indicate the approximate exterior dimensions (including terminals) and voltage of the battery in question. However, the exact dimensions can only be directly obtained from each manufacturer.

Nickel Cadmium Cells

Several people have inquired about NiCad cells for Marine environments. I don't like them due to their high toxicity and low power efficiency.

There you go peoples ;)

Link to comment
Share on other sites

  • 2 weeks later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Who's Online   0 Members, 0 Anonymous, 270 Guests (See full list)

    • There are no registered users currently online
×
×
  • Create New...