RF4LIFE Posted October 3, 2012 Report Posted October 3, 2012 So I have two amps and I'm trying to save money on wire so I don't want more than I need. I'm thinking of only using one really big battery instead of several smaller ones. Im not planning on running the system when the cars off. I'm running a stock 130a alt. with a 1/0 awg big 3 on top of the 4 awg stock wire, i also have a battery tender that I use once a week to top off the battery. I was curious about the wire size vs amperage chart. I wasn't sure if they are using Peak or Rms in finding the total amp draw. I'm using RMS in my calculations, should I use peak instead? I also read that a single run of 1/0awg wire will hold up to 350 amps before melting and their for a 325a fuse should be used. Is this 350 amp limit using RMS or Peak? I only want to use one run of 1/0 awg for positive and one run of 1/0 awg for negative. But I don't know if I need to run two of each? I have a 40f cap inline right before the amps ( within a foot). There is a 17foot gap In between the cap and battery that I need to figure out wire size for. I am also using the cap as my distributed block (each amp has a built in fuse, and the cap has 3 1/0 awg positives and 3 1/0 awg negatives). Here's my calculations: Rockford T8004- running 4 rockford T1692C speakers = 400w RMS total output needed from the amp 400w RMS total output needed from the amp @ 50% efficiency = 800w draw from the amp Rockford T2k- running 1 Fi SP418 subwoofer = 2500w RMS total output needed from the amp 2500w RMS total output needed from the amp @ 70% efficiency = 3250w draw from the amp 800w + 3250w = 4050w Total amp draw 4050w / 14.4v = 281.25a (peak performance) 4050w / 12.46v = 325a (325a fuse) 4050w / 11.57v = 350a (350a 1/0 awg wire)
OrionStang Posted October 3, 2012 Report Posted October 3, 2012 You'll be fine. 300amp fuse on each end of the 1/0 run. SMD Super Seller My Feedback Thread
RF4LIFE Posted October 3, 2012 Author Report Posted October 3, 2012 4050w / 300a (the fuse rating) = 13.5 volts, so dose that mean I can't go under 13.5 volts? Or why wouldn't I stay with a 325a fuse, that way I could go down to 12.5 volts?
will77530 Posted October 11, 2012 Report Posted October 11, 2012 because you will never see that 4050
HHR Ed Posted October 11, 2012 Report Posted October 11, 2012 OK, first a few fundamentals. 1/0 awg is good for about 200A at 14ft and 250A at 12ft. That 350A figure you posted is only useful for about 2ft length of wire. And that is based on pure copper cable. CCA is about 15-20% less capacity. Ed Lester ShowtimeSPL Host Showtime Electronics Video MarketingMy old Build Loghttp://www.stevemead...08/#entry511451http://www.youtube.com/showtimespl 5 time dB Drag Finalist Last ride 2007 HHR, current dB 153.5 and bass race 149.4 dB. 153.0 dB on music New Ride, 2008 HHR SS. Build under way. Loudest score ever = 171dB 2009 dB Drag Racing, North American Points Champion
RF4LIFE Posted October 12, 2012 Author Report Posted October 12, 2012 So I need 4runs of 1/0awg? 2pos and 2neg